I have worked with facilities to design loading and unloading areas so that they do not drain to surface water, but rather to containment -- great if a spill occurs and also avoids some problems with storm water permitting.  Similarly, your facility ought to move toward capture of fire suppression water to avoid an environmental catastrophe that would be in addition to whatever fire you might have.
 
Ralph E. Cooper, Ph.D.
Mediator, Attorney & Counselor at Law
9901 IH-10 West, Suite 800
San Antonio, TX 78230
210.558-0555
----- Original Message -----
Sent: Friday, October 25, 2002 11:40 AM
Subject: fire sprinkler systems

Herb, here are some codes and a potential option for you, from my husband,
who's in the fire protection biz. i believe you meant to say "other than dry
pipe: in your request, but my husband commented on those types of systems). 

FYI:  NFPA 13, Standard for the Installation of
Sprinkler Systems, will only allow pure glycerine (C.P. or U.S.P. 96.5
percent grade) or propylene glycol for sprinkler systems connected to
potable water systems. 

A mixture of 50% glycerine and 50% water protects
against freezing for temperatures down to -20.9F, while 50% water/50%
propylene glycol protects down to -26F.  Although still undesirable in the
event of drainage to the stream, perhaps increasing the water
concentration is an option?  antifreeze systems are limited to sprinkler
systems with a volume capacity of 40 gallons or less; so, the actual
discharge of the non-toxic antifreeze agent would be 20 gallons or less for a
50/50 solution. 

Even so, if toxicity is a concern, there are additional alternatives.

In general, I stear clear of utilizing antifreeze systems because the
maintenance is costly over time and you cannot always guarantee that the
mixture in the far ends of the pipes is suitable to prevent freezing.  Here
are some alternatives:

Dry Pendant Heads: Remove the existing antifreeze system and install dry
pendant heads.  If the loading dock is 7 feet wide or less, the area can be
protected with dry pendant heads extending through the heated side of the
outside wall at a 45 angle.  These heads are directly connected to wet pipe
sprinklers in the heated building.  They are designed to extend into
freezing spaces (i.e., a freezer).  The angled orientation will allow them
to throw out to the end of the canopy.  See NFPA 13, A.8.14.7

Dry Pipe Protection: Install a dry pipe valve in place of the antifreeze fill
system.  Annual maintenance is about the same, but the environmental impacts
are less and the guarantee against freezing is much better.  The piping may
need to be slightly revised to ensure proper drainage (dry pipe
systems cannot have trapped piping sections - they must slope to inch
per 10 ft. for proper drainage).

Heat Trace & Insulate: If the antifreeze system is not too large, it can be
heat traced and insulated.  The temperature must be maintained above 40F
but less than 120F.  This is only acceptable for small unheated areas such
as a small canopy and is the least desirable of the above alternatives.

Michelle Gaither
Tech Lead, PPRC
www.pprc.org

* * * * * * * * * * * * * * * * * * * * * * * * * * * * * * * * * * *
p2tech is hosted by the Great Lakes Information Network:
http://www.great-lakes.net
To unsubscribe from this list: send mail to majordomo@great-lakes.net
with the command 'unsubscribe p2tech' in the body of your message. No
quotes or subject line are required.
About : http://www.great-lakes.net/lists/p2tech/p2tech.info
* * * * * * * * * * * * * * * * * * * * * * * * * * * * * * * * * * *